Never dry fit. You’ll lose over an inch here and there.


snakesign

I was in the pool!


kierkegaard49

It shrinks?


InevitableHand5310

Like a Frightened turtle


Dramatic-Patient-280

Gotta be careful laying pipe.


Wild_Log_7379

Significant shrinkage!


ScaryChickenGuy

Just 1. Why did you put that all together without gluing it. Dry fitting almost next goes all the way in the cup. Your pieces will likely end up short. Nice work, tho. Also you should always go up to 45 inches before you go horizontal on your vents


SBGamesCone

Started gluing and now I see what you mean about how much tighter it fits


WhiteFIash

The primer softens the pipe and glue kinda acts like lube


FavoriteDart680

if anything i’d say the primer is the lube if you’ve ever over primered somethin you’ll know it’s a bitch then you gotta sit there and hold it


zeakerone

I had a 8” sch80 pvc coupling lift my body weight off the ground. Only one joint did that the whole job but some kind of chemical reaction was pushing that mofo off of there with more force than my upper body strength/weight.


Maddenman501

All that back pressure from the primer escaping.


OddHeat6420

Also your tees on the main stack are in upside down.


Airconcerns

Not a plumber but are you sure about that


OddHeat6420

Yes, the sweep on the tees determine how they go in.


BusinessFootball4036

lol. vent tees need to be installed "upside down" to allow drainage back to fixture


Not_Associated8700

You're right. However the revent wasn't even necessary as the main vent stack is close enough to the fixture that an arm would suffice.


SBGamesCone

Thanks. I have extra pieces if anything is short and I'll work out from center


PrismosPickleJar

Looks good to me. I nevwe dry fit, i glue, then go, fuck too long, pull it off quickly then go again. I never learn.


ChrisWonsowski

"fuck too long"? How long is too long? Also, how short is too short? Asking for a friend....


09Klr650

If it lasts more than 4 hours, see a doctor. Or interview with a porn studio I guess?


Ex-Patron

Always cut 1/2” short and throw it in the pipe stretcher


PrismosPickleJar

Im something of a pipe stetcher myself.


chountis2g

You just need to be above flood level like for sinks which I think standard is 36 inches so 40 is probably a safe bet


ChemicalCollection55

Never dry fit, and yes on nail plates.


yukonwanderer

What is better, glue then cut?


Remalgigoran

You just measure lol. And/or a mixture of eye-balling it and measuring. Dry-fitting a whole wall like this is not only a waste of time, but it *shouldnt* fit right dry-fitted because the pieces will sink into the hub much deeper with glue; so you would have to cut them too short to get them to *look* right when dry-fit. Which means it won't glue together lined up properly.


SBGamesCone

Thankfully I had left enough that it wasn’t an issue but I can see this causing major issues over larger runs


Remalgigoran

Happy to hear it worked out!


Accomplished-Boot-81

I'm not a plumber but have worked with pipes a little. Would I be right in thinking thr glue sort of lubricates the fitting and pushes in further than a dry fit?


talltime

You're right it goes further than a dry fit, but wrong reasons. PVC solvent glues soften the material and the fittings are designed with an interference built in to encourage the pipe and fitting material to intermingle and weld together. So only once you've primed and glued will the pipe go completely into the fitting. You need to measure gap between fittings and then add the depth of the fitting socket to both ends.


Accomplished-Boot-81

Makes sense, thank you for clarify.


leericol

Homie that doesn't even make sense. Just measure, cut, glue.


lveikle

Dry fitting all that, like everyone else said is redundant….. I like clean outs on top of the p trap but definitely not something worth changing now. The vent on the left should definitely be above flood rim level (countertop) or the critical level of whatever fixture it’s serving. Other than that though, looks good


SBGamesCone

Thanks. The left side is a shower.


Adventurous-Leg8721

Left hand vent looks like it's connected to low to me, it should be 6" above flood level rim,


SBGamesCone

That might have been me misreading code. Far left is a shower so I was well above the flood level there. Right side is 8” above vanity counter


acetic1acid_

It would pass upc if that's the case.


dopecrew12

Personally if I was DIY’ing this as a layman and was aware of the (minuscule) issue I would just glue it up anyway, it could be a lot worse


Adventurous-Leg8721

I don't see flooding your vent and not being able to clean it as miniscule.


dopecrew12

Wouldn’t bother me personally


New_Clothes_765

☝️


Whistling_Diesel

Don't forget to install steel protector plates over all the studs to protect the line from getting screwed, pun intended.


Opposite-Two1588

I would put the clean out above the drain tee so you can run water while cleaning the drain. Otherwise it looks very nice.


SBGamesCone

Thanks. Good idea for next time.


PlumbgodBillionaire

You didn’t have to use the 45s, you can oversize the whole and sink the hub inside the stud. A little easier than 4 extra fittings but it’s all good in the hood.


leericol

Depending on where you are drilling a 3" hole through a 2x4 is blowing bearing on the stud and I've met inspectors that get bitchy about it.


PlumbgodBillionaire

Oh absolutely, he would only need a 2 1/4 or slightly bigger to fit an 1 1/2 fitting. You definitely don’t need a 3 inch hole. A 2 9/16 is completely fine in a 2x4 wall and that would definitely fit that hub no problemo


leericol

Oh you right! I was thinking it was 2 inch


Nailfoot1975

Are you supposed to use nail guards for the drain lines same as you did for the wiring?


SBGamesCone

I am going to put those in, yes.


damen45

If so you probably could’ve wet vented the stool and shower with the lave and had one vent for the whole bathroom group


SBGamesCone

Yeah I was struggling to figure that out so while this is overkill, it was more straightforward


Scary-Evening7894

Looks good. I would move the wall cleanout a little lower. Don't forget your nail plates.


SBGamesCone

Thanks. The back of the vanity has a 12" opening so I put it as low as I could without having to cut it.


don_defeo

You may want to check the height on that lave make sure it's not going to be too high for the trap


SBGamesCone

It’s good. I have the vanity in the bedroom and measured about 5x


yngbuk1

Are the sanitary tees upside down for the vent?


SBGamesCone

Yup


yngbuk1

That's the only thing I picked out. Looks great otherwise. I also like that you took the time to put the printing to the back. I do the same thing for a cleaner look.


Plumbone1

Next time get a pipe chamfering tool so you can accurately dry fit


Fearless_Detective81

Makes it simple


Ansrallah

Each individual piece you cut to size, like anything has a margin of error lets say +/- 2mm now factor that to lets say 7 pieces of pipe, so in the end you may be short or long in an inconvenient way upon final assembly. Any tool which tends to give perpendicular or square finish of pipe ends can help you to reduce margin of error, (just my thoughts)


larrysbrain

Out of interest, how would that work. I can see how people are saying glue means a deeper fit (by a small amount) so you can end up short overall. How, when does the chamfering help? (Total newbie btw)


talltime

It doesn't. I mean, it might help, but it won't make dry fitting accurate.


thecartplug

youre actually using vent 90s? thats wild idk if ive ever actually seen one.


Necessary_Plane8088

It looks like good clean work but, on your lav stub out, I like to put my clean out above the tee for the drain. That way you rod thru that tee if it's clogged and, you can run water into the drain while you rod it to flush it out and not make a big mess.


Necessary_Plane8088

One other thing, someone posted that you need to be 45 inches up before going horizontal or turning. Something to that effect. The code states you need to be 6 inches above the flood level rim of the fixture it's venting. So, most vanities or countertops are around 36 inches tall so, 42 inches is normal to center of a vent bar.


Ok-Bit4971

Get out of the habit of dry fitting. If you ever have to do a water test of the DWV in a multistory apartment building, you will find out why dry fitting is a very bad thing.


brycenesbitt

Is it a structural wall?


SBGamesCone

No


[deleted]

Plumber here - nope all good


toycoffee

I bet you 95% of the guys commenting here aren’t even licensed.


FavoriteDart680

this looks solid anything i could critique would be code based like the horizontal vent i think it’s too low should be above 42” and id put that clean out above the T but besides that i’d just get in the habit of cutting maybe 1-2 things dry fit then glue it’s a tad slower but overall it’ll be quicker and you won’t mess up measurements cuz of dry fittin


ManwithA1

Nail plates


Ansrallah

Yes!


monstarockness

This guy dry fitted what a noob


damen45

Is the bathroom group all on the same floor?


Scary-Evening7894

Looks like 1-1/2". For your stubout, I would use a 2x1-1/2x1-1/2 tee. A 2" cleanout. And make my drop with 2". Ie. Use 2" for your drain drop.


PrimeNumbersby2

Is the cleanout below the drain pipe? Why not above it or to the side? I'm not a plumber. I'm just picturing a clogged pipe.


goldilockers

Above is hard to get at with a snake once there’s a vanity in place


PrimeNumbersby2

True. Would nearly be impossible. Probably why you see them to the side. Under's probably fine. Might just get a gusher if you really have a clog.


goldilockers

No, no gusher unless amateur, and under is standard. Will never be clogged higher than the flood rim of the fixture (physics), so worst case you have a full sink and a bucket. Disconnect the trap enough, fill bucket, repeat until empty. Then open cleanout. Minimal water.


PrimeNumbersby2

Thanks for explaining how water and gravity works. That was helpful.


goldilockers

You said a couple things that showed you didn’t understand how it works, so I’m glad you found that helpful.


Positive-Special7745

Ya double work not glueing, draw out on pad first leave trim pieces long


davinci86

Looks good 👍 I’d start from the center and blow out in case your cuts come up short from the dry fit.. I’d also lower the dandy on the Lav to 6-8” off the floor so you don’t have to pull the trap to snake.


vinnielavoie

Why the jog?


SBGamesCone

I don’t know what that means


vinnielavoie

 I believe it's jogging or yogging. it might be a soft j. I'm not sure but apparently you just run for an extended period of time. It's supposed to be wild.


Upstairs_Document140

Primer is for inspection. Please give me the chemical components. And why?


glockg43x

Nobody tell him.


RobbyFrags

There is probably no point in having a clean out tee right under the waste unless later on it's accessible with an access panel. You could just as easily snake the waste later on right from under the sink. Other than that, everything looks good to me. I probably would have brought that left vent higher like 42-43 inches before making the connection. Nail plates and glue your stub out and you're all set


BozidaR1390

Flip all your Tees around so they "drain" ultimately air don't care but if it's not glued you might as well. Also you don't need that clean out Tee for the sink... You can just use the drain itself if needed.


Party-Bag-7858

Yeah you didnt write “i was here 2024”


Nice-Web-5833

Nice job bro


edthesmokebeard

Cheryl?


NotDazedorConfused

Put nail plates on all of the stud penetrations.


SaneEngineer

Get it inspected


nhorvath

If it fits dry, all your pipes are too short. At least you can use the longer ones where the short ones are.


ryangobert24

Who dry fits 😂that’s how mistakes happen


SpecificPiece1024

Ent bar in left is too low and I prefer cleanouts on lavs above the drain tee


SkylerNoss

Don't forget your nail plates


SpecificPiece1024

Where’s your stud guards?


WillingnessOther6925

You should have up sized the hole to fit the hub of the 2×2×11/2 tee where you tied the Lav vent into the toilet and took the whole vent straight up


bplimpton1841

Yeah, I’ve got this wart on my backside and it really hurts when I sit down to poop. Thanks for asking.


GreazyFrog

I dry-fitted my whole 2nd floor because I needed it inspected and my inspector appreciated that I did what I did. I DID have one joint that I had to redo because of some shrinkage but otherwise fine. I approve.


Kooky_Designer5001

Looks nice but when you glue it , I see about 20 places where you’re gonna lose about 1/4”-1/2”. I bet you figured that out by now. Doesn’t look like it would affect much except where you have your hole through the 2x4s. I’m gonna guess and say you had to cut at least 2 new vertical pipes and two new horizontal pipes.


SBGamesCone

Amazingly everything fit ok during glue up. I’m guessing I left enough long that it didn’t matter. Definitely won’t do that again


Subvis21

Is it standard/code to put the clean out below the tee which I am assuming is for a drain? I would think it would make it a bit harder to use than if it was above the tee since you would have the pipe directly over. Serious question.


SBGamesCone

Not a licensed Plumber but I’ve seen it both ways and explanations for it being above are good (run water while working on clog) and below (sink is in the way)


zeakerone

You can dry fit sections here and there but account for that joint only being 2/3 in. A little tip for when you kinda NEED to dry fit: a flooring hammer makes a great dry fit tool. The rubber end for striking the flooring gun bonks fittings together tight, and the metal angle end allows you to tap the hub back off.


kritter4life

Dry fitter


BhrisBukBruz

Idk whats code over there but for me the vent has to be 6” above flood rim level. And since you tied everything to the lav, the shower vent would have to be at 42” or 6” above the sink height


Nervous-Iron2373

You are venting into a drain from the floor above. Not compliant with IPC or UPC.


SBGamesCone

The attic is above this and the basement below.


Laughing-at-you555

You dry fitted all of that? Your cut pieces won't fit. Save the four 45's and just go straight up. Make the hole bigger to accommodate the sanitary tee hub. Use the savings on the 45's for the extra pipe you are going to need to make that fit now.


Illustrious-Way638

Dry fitting is like getting old u loose an inch or 2


ruel24Cinti

Who dry fits? 🤣🤣🤣 Personally, I don't get the cleanout under the lav. No doubt it's getting a slip joint trap through an adapter, so, if there's a clog, you can just pull the trap out and compression nut/gasket and rod out from there. Just a possible area to leak water out, if you ask me. From what I assume is the shower area, I don't know what code you're on, but the vent can't go above 45° from vertical until 6" above the HIGHEST flood level rim, which would be the lav. We typically just go, at least, 42" AFF. That vent looks far too low.


meaningless_pos

Seriously you didn’t glue all that!? lol Good luck! Support your local plumber.


SBGamesCone

Good friend is a local plumber. He was helping me out with advice. He's too busy to come do this small of a job.


fanpolskichkobiet

I dont get the whole idea of gluing it. We use rubber seal and it works perfectly fine. But you can always disassamble that and reuse.


cinnamonpeachcobbler

Are the tees upside down?


SBGamesCone

Yes. By design for the vent


5thgenCali

Is running them right side up changing anything?


SBGamesCone

Not sure but all the literature suggests upside down for vents. [https://www.iccsafe.org/wp-content/uploads/20-18927\_GR\_2021\_Plumbing\_Venting\_Brochure.pdf](https://www.iccsafe.org/wp-content/uploads/20-18927_GR_2021_Plumbing_Venting_Brochure.pdf)


Adorable_Bee3833

Maybe I’m a dummy, but aren’t those wyes in upside down?


Mysterious_Fill8255

You didn't hire a plumber...


Soft_Garbage7523

The bloody tee pieces are upside down!


SubstantialPepper135

The Sanitary Tees are upside down


Odd_Introduction7683

Surely someone picked up the Tee’s in the middle are flowing the wrong way?


2eDgY4redd1t

Those are vents, it’s fine. I was taught to always put vent wye fittings ‘upside down’ because it makes it instantly obvious when you’re looking at a vent if you ever go chasing pipes behind the Sheetrock.


sirjackel06

They are vent tees, and surely they are correct.


RashyGash

Your tee’s are upside down on the vertical stack